So I'm working on a 1970's Church Baptistry (full submersion) pool heater/pump system. The system uses a 240V (actually 208V on this service) 6KW heater element, and a circulation pump to heat the water. It was connected with old cloth covered NM cable, 2-#10 wires plus a tiny ground), which I have replaced properly with conduit and #10 THHN. The heater unit is wired to a dryer type plug, and plugged into a receptacle below the Baptistry (5ft above slab). I ordered a 2-pole GFCI circuit breaker since the old breaker was not GFCI, but the system has no neutral connection--only ground to the chassis. Will the GFCI work with no neutral connected to the load? I have search all over the place for a schematic of an actual GFCI so I could see for myself (from and engineering standpoint) if it will work, but can't find one, at least not for a 2-pole circuit breaker like this.
I don't normally do pools, but rather technical power systems, so I just want to make sure I haven't missed something!