Anywhere in NEC that would prohibit securing EMT to them?
Many times we are not allowed to secure anything from the bottom chord of bar joists. This is a building code / manufacturers thing.
You can't run conduits or cable on top of the bar joists in the deck webbing anymore.
Only if it's roof decking. Floor decking is okay but most of it's not deep enough to use.
You can't run conduits or cable on top of the bar joists in the deck webbing anymore.
'08 nec 300.4(e)it's been awhile since i've worked in a building with webbed decking. When did this change and what's the code reference?
'08 nec 300.4(e)
You can't run conduits or cable on top of the bar joists in the deck webbing anymore.
Do you mean above the top chord of the bar joist (in the deck "waffle") or in the space between the top and bottom chords?
According to 300.4(e) (thanks again to rcarroll) you can only run in the "waffle" if there is at least 1 1/2" of clearance from the decking to the EMT or cable, and I haven't seen many corrugated decks with that much clearance. Between the top and bottom chords is still acceptable.