i just received a spec sheet on a particular project requiring bare egc's inside of conduit on all runs. Since when is it acceptable to install bare wires inside of conduit? dont ALL conductors need to be insulated?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: bare egc in conduit

I seem to recall there are a few cases where it is prohibited to have a bare AL EGC - such as underground, or in a metal conduit (disimilar metals maybe).

Or maybe my rememberer is off base.
 

badjeepr

Member
Re: bare egc in conduit

i swear i remember something about (all conductors in conduit to be insulated)..but i cant find any documentaion supporting
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: bare egc in conduit

badjeepr you might of read it in some IEEE standards like the Emerald or Green book, but nothing in the code.

[ September 22, 2005, 06:39 PM: Message edited by: dereckbc ]
 

bob

Senior Member
Location
Alabama
Re: bare egc in conduit

Peter
I seem to recall there are a few cases where it is prohibited to have a bare AL EGC - such as underground, or in a metal conduit
You never put bare AL underground. It would not last long.

I belive that bare EGC in metal conduit is to be bonded to the conduit at specified distances to prevent arcing under fault conditions.