Bare EGC

Status
Not open for further replies.

jes25

Senior Member
Location
Midwest
Occupation
Electrician
Hey Guys,

I have a project where they guys ran a bare EGC inside of a raceway. The inspector says it has to be insulated. Is he correct? The raceway is non-metal sealtight.
 
What is the circuit feeding? If it happens to be swimming pool equipment the inspector is correct.
 
There was a code # in 2005 that stated all conductors in conduit shall be insulated but I can't remember it. I'll look it up.
 
Since you mentioned generator, just to clarify, we are speaking of the grounding conductor and not the grounded or neutral conductor ?
 