250.118 Types of Equipment Grounding Conductors.
The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:
FPN: For effective ground-fault current path, see 250.2 Definition.
(1) A copper, aluminum, or copper-clad aluminum conductor. This conductor shall be solid or stranded; insulated, covered, or bare; and in the form of a wire or a busbar of any shape.
Is there anything in the NEC that prevents me from running a bare copper equipment grounding conductor through a nipple for a sub-panel?
Is there anything that prevents you from using the nipple? :wink:
Is there anything in the NEC that prevents me from running a bare copper equipment grounding conductor through a nipple for a sub-panel?
Is there anything that prevents you from using the nipple? :wink:
...as a ground.![]()
I have no NEC art , But it is my recollection. #8 bare solid is not allowed in conduit with current carrying conductors. (or nipples)
310.3 Stranded Conductors.
Where installed in raceways, conductors of size 8 AWG and larger shall be stranded.
Exception: As permitted or required elsewhere in this Code.
Guess you meant this:
Yeah , that's right. Thanks.:wink:
But what about "else where in the code".:-?