Bare ground in emt

Status
Not open for further replies.

dcooper

Senior Member
Location
Ma
Was wiring a boiler and the inspector mentioned to me it was a violation to change over romex to emt because you can not have a bare ground in emt pipe (assuming you strip it back, which is how I was taught to do it)...
I used mc so it wasn't an issue but it brought up a discussion. He was supposed to email me the the article ( just for my knowledge) but he didn't.
He said it is widely enforced in the city by all 4 wiring inspectors, especially on service changeovers...
I've never heard of this......
Anyone???!
 
Maybe it is a local requirement.
If it is, it would be hard to justify. But then the Chicago and NY rules are hard to justify too.
Bare wire may be harder to pull though.

If the environment is corrosive, a bare wire would be more vulnerable. But they are always bare inside boxes.

mobile
 
Last edited:
EGC's are permitted to be bare and bare conductors are permitted in metallic conduits.

250.118 Types of Equipment Grounding Conductors.
The equipment grounding conductor run with or enclosing
the circuit conductors shall be one or more or a combina-
tion of the following:
(1) A copper, aluminum, or copper-clad aluminum con-
ductor. This conductor shall be solid or stranded; in-
sulated, covered, or bare; and in the form of a wire or
a busbar of any shape.
 
It doesn't make sense to me.... You would run the bare conductor to a ground screw in a metal box..... I gotta email him on this
 
I've heard this same nonsense from a city inspector in RI, although it was only stated that you can't run NM cable in a raceway. :roll::roll:

I'll say it again - there's a reason why some of us will avoid permits and inspections wherever possible.
 
You might not want to do it, though. The pull might be more difficult with a solid bare copper ground in the bundle than it would be with a green stranded THWN-2, especially if it's not a straight pull.
 