I have a situation set up like this: 480v 3 phase 200 amp service. In the conduit from the power company's transformer, there are three 250 AL wires and a bare #4 copper. These enter a CT cabinet, then continue to a 200A service disconnect. Currently, the bare wire is bonded to the CT cabinet, and also to the main disconnect switch enclosure. So there is presently no grounded conductor installed. The load does not require a grounded conductor, (neutral) but the NEC codebook does.
Is there a way to make this legal without pulling another wire? For example: take the bare #4, land it in the CT as if it were the grounded conductor, (230.41) then bond the can, continue into the disconnect, land it on a neutral bar kit and bond the enclosure. I know you can use a bare wire for the grounded conductor, but then should it have white or gray tape to identify it as the grounded conductor?
Thanks guys.
Is there a way to make this legal without pulling another wire? For example: take the bare #4, land it in the CT as if it were the grounded conductor, (230.41) then bond the can, continue into the disconnect, land it on a neutral bar kit and bond the enclosure. I know you can use a bare wire for the grounded conductor, but then should it have white or gray tape to identify it as the grounded conductor?