Under the NEC, can the neutral of a system over 1kv, buried underground, be bare?
Not sure about NEC, but utilities used to use open concentric medium voltage direct burial cable all the time. The neutral is unsheathed bare copper wires wrapped around the insulated center phase conductor. Most use a jacketed "unishield" design now, which uses copper foil instead of wire. Less prone to damage, and can be pulled through conduit.
250.184 Solidly Grounded Neutral Systems. Solidly
grounded neutral systems shall be permitted to be either
single point grounded or multigrounded neutral.
(A) Neutral Conductor.
(1) Insulation Level. The minimum insulation level for neutral
conductors of solidly grounded systems shall be 600 volts.
Exception No. 1: Bare copper conductors shall be permitted
to be used for the neutral conductor of the following:
(1) Service-entrance conductors
(2) Service laterals or underground service conductors
(3) Direct-buried portions of feeders
Exception No. 2: Bare conductors shall be permitted for the
neutral conductor of overhead portions installed outdoors.
Exception No. 3: The grounded neutral conductor shall be
permitted to be a bare conductor if isolated from phase
conductors and protected from physical damage.
Even though the NEC may allow a buried neutral allow for service I would check with the inspector I do know that in my area it is no longer allowed if im not mistaken knob and tube wiring is still in the code but again no longer allowed at least in my area
Most important part of that statement is the fact it was for "over 1000 Volts"This is for systems and circuits over 1000 volts