I'm working in a new house with a barn door covering a receptacle when the door is in the open position. It seems like poor design and a hazard for any cord plugged into it. However, does anyone know of a code reference I can use to support moving the recep? It's a 36" door, so we can easily move the recep and still be within 72" of the door R.O. Thank You.
 
Not exactly the same, but here we don't have to place a receptacle in a space that will be covered by an open door. The wall measurement starts at the edge of the door when opened.
Maybe your (OP) jurisdiction has a similar exception.
 
Here, the door itself is ignored, but the 6-12-12-6 rule still allows the receptacle to be placed beyond the open door.
 
Not exactly the same, but here we don't have to place a receptacle in a space that will be covered by an open door. The wall measurement starts at the edge of the door when opened.
Maybe your (OP) jurisdiction has a similar exception.
The problem is, at rough you don't always know which way the door is going to swing.
 
Interesting. A recp behind a door is OK, not likely to put a table there. But a table could be placed off the wall so the door would roll behind it, and that recp would be blocked.
The solution is a floor recp. I'll make a note and propose that for our state rules next fall for the 2020 NEC.
 
The problem is, at rough you don't always know which way the door is going to swing.

Then you're in trouble because you need to know which side to put the switches on.
I always have the GC or framer, or owner, mark the hinge side of the door so I know which way it swings.

Even if there happens to not be a switch at the door I find out which way it swings just for the reason of receptacle spacing.
 
Then you're in trouble because you need to know which side to put the switches on.
I always have the GC or framer, or owner, mark the hinge side of the door so I know which way it swings.

Even if there happens to not be a switch at the door I find out which way it swings just for the reason of receptacle spacing.
And occasionally they still end up changing it on you. :blink:
 
Flat Cord Plug

Flat Cord Plug

I ran into that once and used a flat right-angle cord plug to easily fit between the door and the wall when the door is open. Agree it is PPPP but not unusable.

A recessed receptacle (old wall clock socket) might also solve some clearance problems.
 