I looked at a barn yesterday (several, actually), and they asked for a quote on some work. I've attached a seriously crude sketch of the distribution.
This is not a commercial agricultural operation. It's a family deal, an older couple with a small amount of livestock mainly as pets, including (1) goat, (1) horse, (?) chickens, (4-6) cows, and (1) pot-bellied pig named Wilbur. A donkey passed away the night before I got there, so he doesn't count. The barns are good sized, and quite roomy, I would think, for this quantity of animals. On a close look, the wiring is a nightmare.
Distribution, generally:
HOUSE breaker panel -> Barn A
underground, looks like URD or some kind of aluminum triplex, in EMT where visible, on double-pole 50-amp breaker in house panel
At building A, terminates in 6" PVC j-box on outside wall of A. no breakers in barn A or thereafter.
GFCI receptacle in additional box mounted on J-box.
Cable connected to GFCI load terminals feeds through wall to inside of A, and then feeds several lights, switches, and receptacles, all wired on 14ga UF.
Barn A -> Barn B
Same kind of feeder as from house to A, in EMT where visible.
Terminates at B in 6" PVC j-box on outside of building.
GFCI receptacle in additional box mounted on J-box.
Cable connected to GFCI load terminals feeds through wall to inside of B, and there feeds several lights, switches, and receptacles, all wired on 14ga UF.
Barn A -> Henhouse
Additional cable connected at barn A j-box, when I got there connected to line side of GFCI, feeds to detached henhouse via 1/2" EMT barely buried and obviously in poor condition.
The GFCI receptacle on A had been damaged due to water. Replaced it, reconnected henhouse to GFCI load; tripped. Left henhouse disconnected.
I realize, and told them, that there's a whole lot of problems here, the worst being a whole lot of 14ga wire on a 50-amp breaker, using the ground for a neutral.
Told them
1) they need small outdoor breaker panel on barn A, instead of the j-box, with proper grounding, feeder configured for 120volts and an insulated neutral, and 15-amp breakers for each building, as all the "branch circuit" wiring was only rated for 15 amps.
2) there's a ground-fault on the henhouse line, either "underground" or in the henhouse, that has to be located and corrected. Also, the "underground" line needs to be underground.
I am completely open to any comments and/or suggestions. Please.
This is not a commercial agricultural operation. It's a family deal, an older couple with a small amount of livestock mainly as pets, including (1) goat, (1) horse, (?) chickens, (4-6) cows, and (1) pot-bellied pig named Wilbur. A donkey passed away the night before I got there, so he doesn't count. The barns are good sized, and quite roomy, I would think, for this quantity of animals. On a close look, the wiring is a nightmare.
Distribution, generally:
HOUSE breaker panel -> Barn A
underground, looks like URD or some kind of aluminum triplex, in EMT where visible, on double-pole 50-amp breaker in house panel
At building A, terminates in 6" PVC j-box on outside wall of A. no breakers in barn A or thereafter.
GFCI receptacle in additional box mounted on J-box.
Cable connected to GFCI load terminals feeds through wall to inside of A, and then feeds several lights, switches, and receptacles, all wired on 14ga UF.
Barn A -> Barn B
Same kind of feeder as from house to A, in EMT where visible.
Terminates at B in 6" PVC j-box on outside of building.
GFCI receptacle in additional box mounted on J-box.
Cable connected to GFCI load terminals feeds through wall to inside of B, and there feeds several lights, switches, and receptacles, all wired on 14ga UF.
Barn A -> Henhouse
Additional cable connected at barn A j-box, when I got there connected to line side of GFCI, feeds to detached henhouse via 1/2" EMT barely buried and obviously in poor condition.
The GFCI receptacle on A had been damaged due to water. Replaced it, reconnected henhouse to GFCI load; tripped. Left henhouse disconnected.
I realize, and told them, that there's a whole lot of problems here, the worst being a whole lot of 14ga wire on a 50-amp breaker, using the ground for a neutral.
Told them
1) they need small outdoor breaker panel on barn A, instead of the j-box, with proper grounding, feeder configured for 120volts and an insulated neutral, and 15-amp breakers for each building, as all the "branch circuit" wiring was only rated for 15 amps.
2) there's a ground-fault on the henhouse line, either "underground" or in the henhouse, that has to be located and corrected. Also, the "underground" line needs to be underground.
I am completely open to any comments and/or suggestions. Please.