I believe a barrier is required for these different voltages in a single enclosure, i.e. switch box, but I can't find the art. # in the code book. Anyone know the art. number?
bill@nkapc said:I believe a barrier is required for these different voltages in a single enclosure, i.e. switch box, but I can't find the art. # in the code book. Anyone know the art. number?
bill@nkapc said:I believe a barrier is required for these different voltages in a single enclosure, i.e. switch box, but I can't find the art. # in the code book. Anyone know the art. number?
That statement is way too general. If the 24 volt system is an Article 725 Class 2 system, it can't be in the same raceway or enclosure as the 120 volt wiring, no matter what the insulation rating of the 24 volt conductors is, with some exceptions. You really need to look to 725.55 as Bob stated in his post.There are times when 24 volts can occupy the same enclosure as 120v. One of the conditions is that the insulation on the 24 volt wire is rated as high as the insulation on the 120v conductor--
don_resqcapt19 said:Dennis,
That statement is way too general.
Because they only read 300.3(C)(1) and not its FPN.I hear this all of the time from electricians in the field. I wonder why so many forget about the separation requirements of Class 2 & 3 circuits.
We all know 300.3(C)(1), read it and don't see the FPN at the end.infinity said:I wonder why so many forget about the separation requirements of Class 2 & 3 circuits.:-?
The use of the exception lets you install the Class 2 or 3 circuit as a Class 1 circuit and yes the circuit must be installed using a Chapter 3 wiring method, but it is still a Class 1 circuit and 725.26(B) tells you that in general Class 1 circuits cannot be installed with power circuits. 725.26(A) only applies to two or more Class 1 circuits within a common raceway or enclosure.I believe 725.26(A) would permit it. Once you reclassify you have a Class 1 circuit that must comply with Chapter 3- (725.25)