DJMJ

Member
16' of baseboard heat @ 250watts/ft = 4000w
4000w @ 240v = 16.6amp
NEC 424-3(b) 125% = 25amp Breaker
NEC 240.3(b) = 12/2nmb wire

Look Correct?
 

Volta

Senior Member
Location
Columbus, Ohio
16' of baseboard heat @ 250watts/ft = 4000w
4000w @ 240v = 16.6amp
NEC 424-3(b) 125% = 25amp Breaker
NEC 240.3(b) = 12/2nmb wire

Look Correct?

DJMJ, welcome to the forum!

Your numbers are good, but it is 240.4(D)(5) that will stop you from using #12.
 