Looking for some advice. Came upon an old house with 240v baseboard heating. There is one run that consists of a 30 amp breaker on 10/2 that goes to a junction box and splits to 2 separate 12/2 runs that each go to a separate mysa thermostat. One of the thermostats controls 2 heaters totally 2500 watts (10.85 amps) and the other controls a 2000 watt (8.3 amp) heater. Does anyone have a problem with the 10/2 to 12/2 split? I also called the mysa company and they said it should be fine because the thermostats are rated to 3800watts each and 20 amps. Even though each thermostat is handling way less than 20 amps each. They terminate at. 30 amp breaker.