I have 1.25kw, 1.25kw, 1 kw, 1 kw baseboard electric radiation manufacturer Vulcan model SBF/SBT at 277V supplied from one branch circuit.

Looked at 424.3(A) NEC 2017 but still confused. It says individual branch circuits. Not sire if I have individual branch circuits or not. Total load is 4.25kw. Total FLA is 16.24A. Continuous load is 20.3A. Breaker size should be 25A but provided is 30A breaker.

Is 30A oversized based off of 424.3(A) NEC 2017 version?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
424.3
Branch circuits supplying two or more outlets for fixed elec tric space-heating equipment shall be rated not over 30 amperes. In other than a dwelling unit, fixed infrared heat‐ ing equipment shall be permitted to be supplied from branch circuits rated not over 50 amperes.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
How can you understand quantum physics and not " branch circuits shall not be rated *******" ?? :)
The branch circuit (the circuit feeding space heating equipment) shall not be...... (not to exceed)
 