crashingace
Member
- Location
- United States
I am second guessing myself right now. I had one of my guys install 2 8' baseboard heaters in a bonus room over a garage. he installed a Honeywell TL7235A1003 non programmable t-stat. The owner is complaining that sometimes the room gets up to 80 and the stat reads 72. I sent my guy back out to look into things and he could not find anything wrong so he just changed the t-stat out. The customer called back and the same thing was happening. I went out with my guy to figure things out. I brought our thermal image with and found that there was a cold draft coming into the box that the t-stat was in. so we spray foamed the box up to keep the draft out. as i was looking around the room i noticed that the baseboard heaters were putting out heat and the t-stat was not calling for heat. so we did a little more investigating. We found that the stat would break both legs when shut off then on a call for heat it would close both legs once the stat was satisfied it would only break one leg?? it is listed as a DPST stat. with one leg at the base board all the time would it put heat out? I would think no as the circuit is not complete without the second leg but how else would there be heat coming out of the baseboard when there is no 240 present?? any help on this matter would be greatly appreciated.