I have NEC 2014 section 240.64(F)(3) arrangement where conductor from main service disconnect neutral bar goes to external ground bus bar. From bus bar one conductor goes to grounding electrode. Please see attached sketch. The incoming service conductors are 5 sets of 600kcmil
In the attached sketch conductor from external busbar to concrete encased electrode labeled “size” in attached sketch what size should it be based on NEC 2014? #4awg or 3/0 awg? I looked at NEC 2014 section 250.66(B) but its confusing I have bonding jumper NOT grounding electrode conductor according to NEC 2014 section 250.64(F)(3) from external bus bar to grounding electrode so not sure if NEC 2014 section 250.66(B) applies or not.
In the attached sketch conductor from external busbar to concrete encased electrode labeled “size” in attached sketch what size should it be based on NEC 2014? #4awg or 3/0 awg? I looked at NEC 2014 section 250.66(B) but its confusing I have bonding jumper NOT grounding electrode conductor according to NEC 2014 section 250.64(F)(3) from external bus bar to grounding electrode so not sure if NEC 2014 section 250.66(B) applies or not.