I would like to point out that, technically speaking, the GFCI's did not fail to operate (test button aside): nobody was receiving a shock. There was no pathway back to the neutral, and the power cords contain no EGC. All that was proven is that the drain system is not grounded and/or contains plastic.tallgirl said:While on You Tube I found two interesting, non-humourous, videos from our own Joe Todesco --
http://www.youtube.com/watch?v=oFUgveAdB2k
http://www.youtube.com/watch?v=-M8fFzl365Q
Now we know what he does when he stays in hotels ...
...as long as the combined total impedance of the pathway through the body, floor, etc. was approx. (120/0.005) 24K or less.stickboy1375 said:... had someone put their hand in that sink (which I wish they had) the gfi would had tripped...
stickboy1375 said:I agree... had someone put their hand in that sink (which I wish they had) the gfi would had tripped...
tallgirl said:What, you don't like Joe?!?
That's one thing I don't understand about GFCIs and two wire devices. If you're in a tub with no connection back to ground -- like, if your plumbing is PVC from the drain on down -- what's the point? Or maybe that is the point -- the lowest resistance path is inside the blow dryer.
On a more interesting note, I was surprised that the blow dryers worked as well as they did in the water. I forget the density conversion between water and air, but water is a LOT denser than air.
I went down a set of basement stairs once for a service call. I already knew that the basement had water in it, so I had rubber boots on. To my surprise, I saw a power strip, plugged into a GFCI, on while it was underwater. The light on the switch was still glowing. Gulp...acrwc10 said:No impuritys no cuntuctive.
No, it's for equipment grounding/fault protection. The circuit breaker (or over-current portion of a GFCI breaker) is for OCP.stickboy1375 said:The ground on a GFI is for OCP only...
Well, yes in the sense that one device does both functions: ground fault and overload. The EGC has no funtion in over-current protection, only equipment ground faults.stickboy1375 said:I should have reworded that...I meant to say, provides a low current path for the OCP to open...