Bath Circuit

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I have a structure which has bath & bed and "general" area but no provisions for cooking which, to me, seems it would be classified as a "guest room".
(There are several of them on a property with separate kitchen). The bath general area receptacles are on the same circuit. From my read this is permissible.
Am I correct ?
 

Barney B

Senior Member
Location
Hurst, TX
Occupation
Electrical Instructor/Trainer
Yes. If this is part of a dwelling unit, NEC2020 210.11(C)(3) would require this to be a 20-ampere circuit.
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
Cooking? Yes, we like Bath Buns. Sally Lunns buns. One of the oldest oldest houses in Bath.
Mods, forgive my frivolity.................
 