jaylectricity
Senior Member
- Location
- Massachusetts
- Occupation
- licensed journeyman electrician
Quick version:
I installed a Broan/Nutone bath/fan/heat that in the instructions says to use a dedicated 20A circuit. Because I'd have to run a 12-3nm and a 12-2nm to have 3 switches I like to just give the heater a dedicated 15A using the 2- wire for that and put the fan/light on a 14-3 using the lighting circuit.
Are there any official documents out there by the manufacturer that state it is ok to do it this way?
More info:
Instead of 7 #12 conductors in the tiny junction box with one neutral unnecessary I have 7 #14 conductors.
I have a 12A fan fed by a dedicated 15A circuit
I have the fan/light, a wafer LED and a vanity light supplied by a dedicated 15A circuit
In my opinion the manufacturer's instructions are for people who need the instructions. My wiring method is safe and effective.
The inspector saw the wiring on rough, but claims he didn't know there was a heater involved. Not sure how you don't see the heating element as it is prominent.
But understandably he doesn't want to put his or the town's name on it for liability reasons.
To fix it we'll have to open up the tiled floor for the home run, the wall for the switches and the ceiling for the unit.
I understand the letter of the law, but there will not be a problem. Most inspectors understand this. Yes, I should have found out if he'd be ok with it beforehand.
I installed a Broan/Nutone bath/fan/heat that in the instructions says to use a dedicated 20A circuit. Because I'd have to run a 12-3nm and a 12-2nm to have 3 switches I like to just give the heater a dedicated 15A using the 2- wire for that and put the fan/light on a 14-3 using the lighting circuit.
Are there any official documents out there by the manufacturer that state it is ok to do it this way?
More info:
Instead of 7 #12 conductors in the tiny junction box with one neutral unnecessary I have 7 #14 conductors.
I have a 12A fan fed by a dedicated 15A circuit
I have the fan/light, a wafer LED and a vanity light supplied by a dedicated 15A circuit
In my opinion the manufacturer's instructions are for people who need the instructions. My wiring method is safe and effective.
The inspector saw the wiring on rough, but claims he didn't know there was a heater involved. Not sure how you don't see the heating element as it is prominent.
But understandably he doesn't want to put his or the town's name on it for liability reasons.
To fix it we'll have to open up the tiled floor for the home run, the wall for the switches and the ceiling for the unit.
I understand the letter of the law, but there will not be a problem. Most inspectors understand this. Yes, I should have found out if he'd be ok with it beforehand.