Bath Floor Heat

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Can bath floor heat (1.5 amps) be supplied from a bedroom receptacle branch circuit ?
(minimum character adder)
 

HEYDOG

Senior Member
Can bath floor heat (1.5 amps) be supplied from a bedroom receptacle branch circuit ?
(minimum character adder)
It would need to be g.f.c.I. Protected and if coming from a bedroom receptacle depending on when it was installed may already have a.f.c.I. Protection. If it does have a.f.c.I. Protection IMO might cause nuisance tripping problems!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If the controller has GFCI protection, does the supply circuit have to be GFCI
 