Is it permissible to share the circuit for bath lighting with another room's lighting?
Examples:
Hall & bath lights on same circuit
walk-in closet and bath same circuit
All I see is 210.11(C)(3) and it just mentions "receptacle outlets".
Along the same lines.... Where does it say you can have two baths on the same circuit?
The exception kind of implies you can but don't see anything specifically allowing it. Only thing I see is the wording in 210.11(C)(3) says "such circuits shall have no other outlets".
Examples:
Hall & bath lights on same circuit
walk-in closet and bath same circuit
All I see is 210.11(C)(3) and it just mentions "receptacle outlets".
Along the same lines.... Where does it say you can have two baths on the same circuit?
Exception: Where the 20-ampere circuit supplies a single
bathroom, outlets for other equipment within the same bathroom
shall be permitted to be supplied in accordance with
210.23(A)(1) and (A)(2).
The exception kind of implies you can but don't see anything specifically allowing it. Only thing I see is the wording in 210.11(C)(3) says "such circuits shall have no other outlets".