Not technically an electrical question but many electricians do this as part of a bath fan job.
I'm going to replace three fan/light units in a customers house. The fans are on the top floor with unfinished attic above. I found the existing 4 inch duct from each fan ran into one 4 inch duct with a couple of "Y" fittings. I told him each should have it's own duct and offered to install them. Not a difficult job.
My question is, when he asks me why it can't stay the way it is I don't know enough about the subject to provide a good answer.
As a side note. Incredibly, the one duct that runs to the outside was sealed off with a piece of sheet metal where there should have been a flap termination thingamajig. Because of this, each bathroom has been blowing air from one bath to the others. All the ducts are full of dust/debris, so I plan to replace them all.
I'm going to replace three fan/light units in a customers house. The fans are on the top floor with unfinished attic above. I found the existing 4 inch duct from each fan ran into one 4 inch duct with a couple of "Y" fittings. I told him each should have it's own duct and offered to install them. Not a difficult job.
My question is, when he asks me why it can't stay the way it is I don't know enough about the subject to provide a good answer.
As a side note. Incredibly, the one duct that runs to the outside was sealed off with a piece of sheet metal where there should have been a flap termination thingamajig. Because of this, each bathroom has been blowing air from one bath to the others. All the ducts are full of dust/debris, so I plan to replace them all.