Please correct me if I'm mistaken
Bathrooms do NOT require afci protection.
That would include lighting, receptacle, jacuzzi. Anything and everything.
Correct?
Thank you
Bathrooms do NOT require afci protection.
That would include lighting, receptacle, jacuzzi. Anything and everything.
Correct?
That is correct. Branch circuits supplying bathroom outlets or devices are not required to be AFCI protected.
It is uncertain at this point in time if the 2017 NEC will expand AFCI protection to all 120-volt, 15- and 20-ampere branch circuits in a dwelling. STAY TUNED...
Please keep in mind the NEC does not prohibit the installation of AFCI protection for bathroom branch circuits.
Did it pass the comments stage?
Well then industry better come up with 2 pole GFCI/AFCI combo breakers -- existing remodels that change out devices are becoming problematic.
Funny how I ever survived in a house with out it burning up with out all this #@*& protection.
a significant number of people die...
This can be said about any evolving technology. Most people won't die in a car accident or an airplane crash so why make them safer? Most people won't die from brain cancer so why try to find a cure? How many lives does take before we do something about it?
I think you get my point...
This is the same argument that happened at the introduction of the AFCI requirement. Safety at any cost vs. quantifying loss (which the courts do ALL the time).
Bryan, we, the installers of AFCI's are still waiting to be shown how the technology actually works. . . so we can show our clients the value of their purchase.
Bryan, we, the installers of AFCI's are still waiting to be shown how the technology actually works. . . so we can show our clients the value of their purchase.
This can be said about any evolving technology. Most people won't die in a car accident or an airplane crash so why make them safer? Most people won't die from brain cancer so why try to find a cure? How many lives does take before we do something about it?
I think you get my point...
This is the same argument that happened at the introduction of the AFCI requirement. Safety at any cost vs. quantifying loss (which the courts do ALL the time).
Bryan, we, the installers of AFCI's are still waiting to be shown how the technology actually works. . . so we can show our clients the value of their purchase.
A GFCI is does the EXACT same thing as an AFCI.