Was installing a bath ex fan yesterday and noticed that the label said something along the lines of.... acceptable for use in shower if on a GFCI protected BRANCH CIRCUIT.
Of course, the fact that it would need to be GFCI protected is no surprise, but, I must admit, it got me to thinking as to whether or not I can legally have it powered by the load side of a GFCI receptacle. Maybe I'm wrong but I thought a branch circuit originates at OCP, not at a receptacle, which would technically mean that I need to put it on a GFCI breaker.
Thoughts on this?
The
UL White Book gives the exact language that the manufacturer must use in the "Product Marking". Take a look:
GUIDE INFORMATION FOR ELECTRICAL EQUIPMENT ? THE WHITE BOOK
FANS, ELECTRIC (GPWV)
PRODUCT MARKINGS
Ceiling-insert fans, wall-insert fans, and ceiling-insert fan/light combinations intended to be mounted over bathtubs, showers, or within the zone above the bathtub and shower area as defined by Article 410 of the NEC, are marked ??
Acceptable for use over a bathtub or shower when installed in a GFCI protected branch circuit.?? These products are investigated to determine the effects of moisture (dampness or wetting), such as shower spray.
Also, in order to line up the ducks in a row, the 2011 NEC Article 100 Definition of Branch Circuit is:
Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).
As I read the definition of
Branch Circuit I pay attention to the fact that "conductors" is plural, and nothing limits the "hot" or "neutral" or "ECG" to each being a singular conductor. In fact, I read read the definition word "conductors" to include the segments of conductor that usually make up a branch circuit.
That is, each "hot" is made up of segments of conductor, along with the "neutral" and "ECG", and all those segments, some hot, some neutral, some ECG, are parts of the Branch Circuit.
Each segment of circuit conductor is one of the Branch Circuit circuit conductors.
A GFCI device, either a receptacle or a dead front, inserted at some point between the Overcurrent Protective Device (OCPD)and the Outlet (at the bath exhaust fan), has Branch Circuit circuit conductors on both the Line and Load sides of the device.
The exhaust fan is connected to the segment of Branch Circuit circuit conductors that are GFCI protected. That is, the exhaust fan is
installed in a GFCI protected branch circuit.
In another thread, concerning GFCI receptacles connected to a MultiWire Branch Circuit (MWBC), a similar point was raised that the MWBC wasn't an MWBC unless all the conductors of the MWBC went from the OCPD to the farthest Outlet. I think the Bath Fan on a GFCI is a similar conflation.