Bathroom exhaust fans article 220

Status
Not open for further replies.

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
Does a bathroom exhaust fan need to be included in the calculation or does the 3VA/sqft cover it already? Where do you apply bathroom exhaust fans in the calculation? Is it considered a appliance fastened in place?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
See 220.12(A) or 220.14(J) for nondwelling and dwelling occupancies for motors that are 1/8 hp or less. Note these are 2020 code citations.
 