Bathroom GFCI

Kevin.hndz

Member
Location
New york
Occupation
Electrician
Working on this small bathroom and was wondering as you can see there are 2 bathrooms one GFCI for each and one outlet for a electric heater. Would you say I can bring one dedicated feed for the GFCI and then come off the load side to everything else or should I run one dedicated line for each of the gfci's and then load side for the heater
 

Attachments

  • Screenshot_20250801-053551.png
    Screenshot_20250801-053551.png
    260 KB · Views: 20
The bathroom receptacles have 2 install choices
1. Run a circuit to the first bath receptacle and load side to the other
2. Run a circuit to first bathroom and everything in the bathroom is on that circuit. Then run another circuit to the other bathroom. You cannot leave the bathrooms to feed anything else.

Do not install anything but the receptacles on load side of the gfci
 
The bathroom receptacles have 2 install choices
1. Run a circuit to the first bath receptacle and load side to the other
2. Run a circuit to first bathroom and everything in the bathroom is on that circuit. Then run another circuit to the other bathroom. You cannot leave the bathrooms to feed anything else.

Do not install anything but the receptacles on load side of the gfci
Your option 1 is too restrictive. Nothing precludes a home run to each bath. As long as the circuit feeds only bath receptacles, it doesn’t matter (code-wise) how the GFCI gets accomplished.
 
Your option 1 is too restrictive. Nothing precludes a home run to each bath. As long as the circuit feeds only bath receptacles, it doesn’t matter (code-wise) how the GFCI gets accomplished.
Would you say I can run one dedicated line to the first bathroom GFCI then load side everything else downstream
 
Would you say I can run one dedicated line to the first bathroom GFCI then load side everything else downstream
The drawing isn't very good. It shows (guessing) either 208 volt or 240 volt supply to the heater with a thermal switch. Not sure if the receptacles have anything to do with the heat. Since this isn't a dwelling you can wire the receptacles however you choose.
 
The drawing isn't very good. It shows (guessing) either 208 volt or 240 volt supply to the heater with a thermal switch. Not sure if the receptacles have anything to do with the heat. Since this isn't a dwelling you can wire the receptacles however you choose.
According to the GC the heater comes with a standard 120 whip which is why he asked for the recepticle
 
If this is in a school, I would lean towards a GFCI breaker. Kids like to push buttons!
Not only that, but despite all the controversy over gendered bathrooms, I don't think it would be a good idea in a middle school to have to go into one bathroom to reset the GFCI for the other. GFCI breaker solves all issues.
 