Bathroom HLV Conductors

Status
Not open for further replies.

hillbilly

Senior Member
I've got about 30 pieces of 5 conductor type TC direct burial cable averaging 25' long. The conductors are #12 THHN with overall outer jacket.
These cables would be perfect to provide power to bathroom Heat/Light/Vent units. The only problem is there is not a white or green color in the bundle. Is there anything that would allow me to identify the grounded and grounding conductors so that this cable can be used for this purpose?
steve
 
Re: Bathroom HLV Conductors

Steve,
TC cable is not permitted for that use. See 336.10 and 336.12.
Don
 