Bathroom outlets

Status
Not open for further replies.

nathan

Member
In article 210.50(D) I was always under the impression that it ment each basin will have its own recepticle within 3ft of its basin edge, through reading it again (for the 500th time) Im beginning to chane my mind thinking the basins can share the outlet if the y are within the legal limit. Just wanted to see what some others thought . Thanks in advance to any response.
 

bennie

Esteemed Member
Re: Bathroom outlets

One duplex receptacle? one outlet for each basin.

[ July 10, 2003, 12:10 AM: Message edited by: bennie ]
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Bathroom outlets

Hi nathan,

"within (3 ft) of the outside edge of each basin."
Note: Does not say "each and every".

Let's say you have 2 basins and they are installed so that the edge of the one on the right is 6' away from the one on the left, you need one receptacle. (within 3'of the right and within 3' of the left)

Kind of like the rule of 12' for other receptacle spacing.("Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 1.8 m (6 ft) from a receptacle outlet.")

Hope this helps,
Dave
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Bathroom outlets

basin.jpg
 

nathan

Member
Re: Bathroom outlets

Hey thanks guys...fast respponses too......thats kinda what I thought. Im glad I checked it makes more sense.
 