Bathroom receptacles

Status
Not open for further replies.

rlever

Member
What are the placement limits for a GFI receptacle in proximity to a bathtub?

This is for a New Residential home in california.
 
Re: Bathroom receptacles

I'm sure it can't. I was asking if there is a distance that it must be from a bathtub. Do you know?
 
Re: Bathroom receptacles

Article 406.8(C).

Roger
 
Re: Bathroom receptacles

The receptacle can't be in the "bathtub space". Are you checking up on a installation? What is a field auditor (your profile)?
 
Re: Bathroom receptacles

Go to the outside wall of the tub. Draw a line straight up to the ceiling. Recep can be anywhere outside that line. This is per 1999 NEC, I'm not sure what the 2002 will change.
 
Re: Bathroom receptacles

The 99' and 02' restriction is identical, they are just in different sections. (99':410-57(c), 02':406.8(C))

I believe the 2005 will add a change. It may state, "receptacles shall not be installed within or directly over the bathtub or shower stall."

This doesn't change the particular question at hand.
 