This is just a suggestion.
Several years ago an inspector made this observation - it made sense to me and I've been installing receptacles this way for hydro-tubs ever since. I used to install a GFI receptacle next to the motor under the hydro-tub in a master bath. This (in most cases) isn't readily accessable nor is a GFI circuit breaker located in a remote breaker panel readily accessable. He said that he could not site me for a violation but said that if the GFI receptacle (or breaker) happened to trip, the homeowner would have to open the access panel (sometimes located inside a closet adjacent to the hydro-tub motor location) or go to the breaker panel to reset. He suggested that I install a faceless GFI on a wall inside the master bath and feed a standard receptacle next to the motor. That way the GFI feature could be tested on a regular basis.
This is a bit more expensive way to do this and not required by code but it seemed like the right thing to do. Also, if you use a GFI breaker and it happens to trip, you don't know if it trips because of a ground fault condition or an over load. If I had to pick one or the other, I would use a GFI receptacle rather than a breaker.