Bathrooms 210.52(D) and Incorrect Reference: 210.11(C)(3)

Status
Not open for further replies.

Duuk

Member
Location
Texas
Occupation
Journeyman
Please see the attachment.

One or more 120V, 15A branch circuits shall be provided to supply bathroom(s) receptacle outlet(s) required by 210.52(D).

True or False

I picked True and it was wrong.

Why?

Incorrect Reference: 210.11(C)(3)

Thanks for your time…
 

Attachments

  • 37CE1C38-7CBC-4054-9B15-9F8D9A42B1A1.jpeg
    37CE1C38-7CBC-4054-9B15-9F8D9A42B1A1.jpeg
    1.3 MB · Views: 13

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Because bathrooms require 20 amp circuits.

(3) Bathroom Branch Circuits. In addition to the number of
branch circuits required by other parts of this section, at least
one 120-volt, 20-ampere branch circuit shall be provided to
supply the bathroom(s) receptacle outlet(s). Such circuits shall
have no other outlets.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The response is Incorrect--

The Reference for the correct answer is 210.11(C)(3)

It does not mean 210.11(C)(3) is an incorrect reference.
 