In a commercial building, (animal clinic) can I put 3 bathrooms (outlets) on one circuit? Or does each bath outlet need a circuit? (Indiana)
In a commercial building, (animal clinic) can I put 3 bathrooms (outlets) on one circuit? Or does each bath outlet need a circuit? (Indiana)
In a commercial building, (animal clinic) can I put 3 bathrooms (outlets) on one circuit? Or does each bath outlet need a circuit? (Indiana)
Thank you !Note that 210.52, in which sub part D is for bathrooms, is for dwelling units. Also 210.11, in which sub part C is for bathrooms, is also for dwelling units. Between those two sections we have the requirements for 20 amp circuits and no other outlets to be supplied other then bathroom outlets - but they both apply to dwelling units only as mentioned in the title of each section.
There is no similar requirements for non dwelling unit bathrooms. You will need to figure a minimum 180 VA per outlet though for load calculations if there is no specific load intended to be supplied by the outlet.
I actually try to avoid putting receptacles in commercial bathrooms unless the customer or plans specifically mention one. They don't get used like they do in a home. I think the only reason some electricians put them in is because they think a bathroom is a bathroom, if a home gets one, then so should this commercial bathroom.
Eggggggzactlllly. I agree. There is no need for a recpt in a commercial bathroom except to give a place for a homeless guy a place to plug in his cell phone charger.I actually try to avoid putting receptacles in commercial bathrooms unless the customer or plans specifically mention one. They don't get used like they do in a home. I think the only reason some electricians put them in is because they think a bathroom is a bathroom, if a home gets one, then so should this commercial bathroom.
I always do it just because ive always done it, and always see it. Also, because ive had numerous electricians call me tell me one is required and rather then argue, sometimes its just easier to go along with the myth.
If for some reason some needs to make repairs using a power tool, its better that they use a GFI protected receptacle rather then one in the corridor.
Unless the customer asks for it, or it is on the print I do not put one in.
It is only a liability in most cases, not a benefit.
Eggggggzactlllly. I agree. There is no need for a recpt in a commercial bathroom except to give a place for a homeless guy a place to plug in his cell phone charger.
I hope I'm never homeless in DGO. That was pretty insensitive - could be a vet down on thier luck. Still no requirement for a recept per NEC code.
You must not live near a city.
Many bathrooms they put locks on the doors and you need s code. Even restaurants like pizza and sandwich shops, the code will be on the sales receipt.
You'll have to define city -- cause I might be living in a town I know its not a metropolis
So life is beautiful for everyone there? No problem with the local homeless / drug users / drunks taking over bathrooms and trashing them? Must be nice.
Because that is definitely an issue in Boston.