Re: Batteries- fused?
Generally a utility is any company recognized by a city, municipality, state or local government. This is usually done by elections granting the company a monopoly. As a utility they are not required to apply for building permits nor are they ever inspected by an AHJ
As a former SWB and MCI CO power engineer of 24 years all Telco?s has debated this topic several times over the last 100 years. It really comes down to company policy. Most decide not to fuse battery strings because of the outage potential created, complexity in replacing the fuse, and the minimal risk involved.
There are two NEC code issues widely ignored by telephone companies where DC power is involved. One is fusing battery strings; the other is a de-rating conductor for adjustment factors of 310.15.B.2 contained in raceways.
SWB and MCI policy is not to use any fuses in battery strings in central offices. However there are special circumstances where they will be used such as CPE (customer premises equipment) where the facility is not owned or maintained by the Telco, or in co-located facilities where Telco does not own and operate the facility. Again there are even exceptions to this rule if the CPE is a hospital, DOD, police, fire, or civil defense facility where an outage cannot be tolerated.
I understand your concern for an individual?s safety, but once you compare the risk with the possibility, the needs of many outweigh the needs of an individual. A 48 VDC plant does not present much exposure to electrical shock, only some fire danger.
Consider a large 48 VDC plant of say 10,000 amps using 14-4000 ah battery strings, and 16-800 amp rectifiers. Each battery string would require a 2000 amp time-delay fuse enclosed in a disconnect device. From the battery string terminal plate you would run 2000 KCM from each polarity to the disconnect device which contains the fuse. Then from the disconnect device you would again run 2000 KCM to the power plant charge bus a short distance away. The only two places where a fault is likely to occur is on the battery terminals (which is not fused), and the charge bus. At the charge bus you have 14-4000 ah batteries and 16-800 amp rectifiers all in parallel with a fault current availability of several hundred thousand amps if the resistance allows it.
The point here is the only likely place for a fault to be incurred to allow a fuse to operate is at the battery charge bus. It is highly unlikely that even a bolted fault would operate any of the fuses in the batteries due to the resistance of the fault in series with the cable resistance at 48 VDC. From my experience and Telco experience, is the fault is vaporized which acts as the fuse to clear the fault. Yes someone can and will be hurt from the flash, but it would happen even if you had the batteries fused or not. By not fusing you eliminate an outage and protect public safety. Keep in mind these offices are a vital link to public safety including DOD, hospitals, police, fire, civil defense, FAA, long distance traffic, etc.
Sorry to be long winded, but that is the analogy used, not poor engineering.