Batteries Not getting enough charge
Not enough information supplied for us to help you.
Where is the system located?
What is the energy need? If you have a DC system, provide battery voltage and needed amp-hours per day. If you have a AC system, provide battery voltage and needed watt-hours per day.
Please specify the ratings of the equipment you have: PV module ratings, battery capacity.
How was the battery tested? Full capacity test at known load for a specific/measured period? Just a simple load test?
Battery voltages, Morning, noon, and evening would help others understand your situation.
I agree you have not provided any useful information to help you out.
Battery Voltage
Battery Amp Hour Capacity
Panel wattage and specs
Daily watt hour useage
Charge controller Type.
As a general rule of thumb the panels need to supply a C/10 charge rate to the batteries, where C = Battery Amp Hour capacity @ 20 hour discharge rate.
Now with that said is still useless because if you have say a 100 Amp Hour Battery @ 12 volts using 600 watt hours per day, you have a dead destroyed battery in a short time regardless of panel wattage. The system as a whole has to be matched to do the job at hand.
Daily discharge on a battery should be limited to 20%, and panels have to be large enough to fully recharge the batteries during the shortest days of winter, plus enough to recover from cloudy days
For example if you use 1 Kwh/day in Kansas City on a 12 volt system using a PWM Charge Controller you need:
12 Volt Solar Panel Wattage = 600 watts
PWM CC = 40 amps
12 Volt Battery AH Capacity = 400 Amp Hours .
If using a MPPT Charge Controller you would need:
Solar Panel Wattage = 450 watts
MPPT Charge Controller = 40 amps
12 Volt Battery Capacity = 400 AH