Battery cables

Status
Not open for further replies.

Eros

Member
Location
United States
Why do we have to size battery cables on the Ah of the bank dater than the Kw of the inverter and the ability to invert a limited amount of current and charge at a determined amount. The inverter can't draw 300amp from the battery and the CC is limited hits charging current. Just curious
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Why do we have to size battery cables on the Ah of the bank dater than the Kw of the inverter and the ability to invert a limited amount of current and charge at a determined amount. The inverter can't draw 300amp from the battery and the CC is limited hits charging current. Just curious

You don't have to, although it is good practice to allow for putting in a larger inverter later.
There is also a potential issue with short circuit current if you do not have fuses on the battery posts.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
Why do we have to size battery cables on the Ah of the bank dater than the Kw of the inverter and the ability to invert a limited amount of current and charge at a determined amount. The inverter can't draw 300amp from the battery and the CC is limited hits charging current. Just curious

I don't know - it's not NEC. Could it be the owner's spec? Cause if it is - that' a really good reason. Another reason for upsizing the cables is voltage drop. For me, that is more often the limiting factor than NEC ampacity.

As for upsizing for what might happen in the future, that wouldn't matter to me. If a larger inverter is being installed, there is a lot more to look at than just the battery cable size.