I am in the military and newly posted to a shop that performs generator and UPS maintenance on our base. I've noticed that quite a few of our installations were preformed by personnel that were posted in our shop and not by the dedicated installation unit. This has resulted in some minor mistakes in wiring devices such as battery chargers. I want to effectively explain to our new apprentice's what the overall outcome can be in different charging situations with the current setup.
A little background of the charger setup. It is mounted inside a Cummins transfer switch, a harness is used to connect the output terminals of the charger to a terminal block within the switch. The terminal connectors max conductor size is 10 AWG. Connection is made on the starter for the generator.
So in normal operation our 15 amp 12 volt charger will float and output .5 - 1.5 amps of current. During this time the temp rise on the conductor is minimal and the voltage drop at the end of the conductor falls within a specification which allows the unit to function correctly.
Generator fails to start after 3 cranking cycles and the batteries are now drained. The charger kicks on and outputs an amperage between 6 and 12 amps. This causes the conductors to heat creating a larger voltage drop.
With the conductors undersized I can see this going two ways.
1. The voltage at the terminal is lower changing the flow of current and you get an output that still charges your battery but not fast enough to meet some NFPA110 applications; and
2. The voltage drop is so low that the supply voltage is lower than the battery output causing the unit to fail.
a. tripping the battery charger built in DC breaker; or
b. causes the unit to overheat and fail completely.
Is there anything I am missing in my failure explanation or can anyone explain in more detail what will happen in 2? Maybe for 2a the heat of the conductor 2b I'm not quite sure how to explain ie. backwards current draw from the battery in which case a diode within the unit would solve.
Possible solutions I will give them are:
1. 10 AWG conductor to a newly mounted terminal block transitioning to a larger conductor. Upsize the conduit and connect the larger +'ve and -'ve conductor to the starter;
2. Install a smaller battery charger with a max output low enough to satisfy wiring with 10AWG as long as it meets a the level of generator application; and
3. Supply the generator unit with a new run of AC and mount a charger closer to the unit shortening the DC run allowing for a 10A charge.
Any input on this would be great, the more angles I can see the more ways I can lead a discussion on this topic.
A little background of the charger setup. It is mounted inside a Cummins transfer switch, a harness is used to connect the output terminals of the charger to a terminal block within the switch. The terminal connectors max conductor size is 10 AWG. Connection is made on the starter for the generator.
So in normal operation our 15 amp 12 volt charger will float and output .5 - 1.5 amps of current. During this time the temp rise on the conductor is minimal and the voltage drop at the end of the conductor falls within a specification which allows the unit to function correctly.
Generator fails to start after 3 cranking cycles and the batteries are now drained. The charger kicks on and outputs an amperage between 6 and 12 amps. This causes the conductors to heat creating a larger voltage drop.
With the conductors undersized I can see this going two ways.
1. The voltage at the terminal is lower changing the flow of current and you get an output that still charges your battery but not fast enough to meet some NFPA110 applications; and
2. The voltage drop is so low that the supply voltage is lower than the battery output causing the unit to fail.
a. tripping the battery charger built in DC breaker; or
b. causes the unit to overheat and fail completely.
Is there anything I am missing in my failure explanation or can anyone explain in more detail what will happen in 2? Maybe for 2a the heat of the conductor 2b I'm not quite sure how to explain ie. backwards current draw from the battery in which case a diode within the unit would solve.
Possible solutions I will give them are:
1. 10 AWG conductor to a newly mounted terminal block transitioning to a larger conductor. Upsize the conduit and connect the larger +'ve and -'ve conductor to the starter;
2. Install a smaller battery charger with a max output low enough to satisfy wiring with 10AWG as long as it meets a the level of generator application; and
3. Supply the generator unit with a new run of AC and mount a charger closer to the unit shortening the DC run allowing for a 10A charge.
Any input on this would be great, the more angles I can see the more ways I can lead a discussion on this topic.