I'm relocating a batter charger from an existing location within three feet of a panel.
The new location is within 25' and the panel is within sight. I'm not required to install a disconnect, correct?
If I hard wire the connections to a standard 4 square box and clearly mark the cover with panel location and breaker numbers, and clearly mark the breaker as dedicated for the charger, am I good to go?