Npstewart

Senior Member
Im reviewing a cutsheet for a battery charger and see that the one im reviewing says 24v, 10 amps. Does anyone know if that means 10 amps @ 24v, or 10A at the nominal line voltage (120v).

Trying to see how many of these will fit on a 120v, 20A circuit.
 
On a side note it sounds as if you have an array of chargers you are installing - are you doing anything for ventilation or hydrogen offgassing from batteries?

Really good point. Yes, the ventilation system has already been designed.

Thank you both, I figured the input was minimal.
 