Seeing you as senior member here I didn't expect such response from you"Give shock" when you touch both battery terminals (hopefully with the same hand)?
How much voltage? Even a 9-volt 'transistor battery' will make your tongue tingle.
.
View attachment 2572923
In spite of the picture, when are you getting a shock?Seeing you as senior member here I didn't expect such response from you
The answer is probably 'No' nowadays, or that your battery will be grounded by other equipment. But we'd need a lot more detail about the system you are installing.Hey Mike
Should we ground battery negative/positive in a domestic solar system?
(battery terminals give shock).
Inverter is not grounded as there no ground/earthing conductor at all. The power lines coming from grid does not supply any ground either.The answer is probably 'No' nowadays, or that your battery will be grounded by other equipment. But we'd need a lot more detail about the system you are installing.
What grid? where is this located?The power lines coming from grid does not supply any ground
Inverter is not grounded as there no ground/earthing conductor at all. The power lines coming from grid does not supply any ground either.
Are you trying to follow the NEC? Or another safety standard?It's located in Pakistan. Grid meaning utility power
N is likely grounded somewhere on the utility network, but you should ask someone local. There are no RCDs?Usually there is no grounding or earthing or any other protection system employed. Just 2 wires L & N
Being a "Senior Member" here only means you've made it past a certain number of posts without getting kicked out. 250 I think?Seeing you as senior member here I didn't expect such response from you
1) It's a 6kw off-grid solar system. Growatt ( Spf6000) inverter is used.Manual says(GROUNDING INSTRUCTIONS -This inverter should be connected to a permanent grounded wiring system. Be sure to comply with local requirements and regulation to install this inverter. ). It's 230v system single phase.Is this an off-grid or grid tied solar system? What is the system voltage? How much power? What does the inverter manual say about grounding and ground fault detection? Do you have a charge controller? Are DC loads supplied or just the inverter?
Let's also not confuse actual earthing (i.e. installing and connecting electrodes) with system grounding (choice of whether to ground a circuit conductor and which one). Your inverter or other equipment may bond neutral to its PE terminal even if you don't connect a grounding electrode to the PE.
Reasons to bond and ground a battery conductor (usually negative) include providing a fault current path to open a fuse or circuit breaker in case of a ground fault. However if your inverter or charge controller already has ground-fault protective devices they may take care of that or not work correctly if you ground the battery solidly somewhere else.
Are you trying to follow the NEC? Or another safety standard?
N is likely grounded somewhere on the utility network, but you should ask someone local. There are no RCDs
Even if they don't follow the standard you need find it out.2) My scope is to connect the Inverter to grounding following NEC.
I laughedI thank Joe B for his comments-- and I agree, I intended no disrespect. I feel that what I think is a humorous response is sometimes needed, although my sense of humour sometimes veers in strange directions.
No one likes my helen keller jokes- if that helps...I thank Joe B for his comments-- and I agree, I intended no disrespect. I feel that what I think is a humorous response is sometimes needed, although my sense of humour sometimes veers in strange directions.
Me tooI laughed
Ron
I won't mention Sandy, Matt, Phil, and Art.No one likes my helen keller jokes- if that helps...