BATTERY INSIDE GARAGE REQUIREMENTS

ING23

Member
Location
Las Vegas
Occupation
Site Survey Tech
I am working on this job with a Tesla Powerwall3 inside garage by customer request and failed inspection due to Missing Heat Detector interconnect to the house Smoke detector or Fire system. As this is a new home and down here in South Nevada there is no prewired neither a Smoke detector inside garage. Here are my interrogantes: 1 Installing a Heat or Smoke detector inside a garage (at least with this really hot summer in las Vegas) is going to be annoying for the customer. 2 Any Idea how comply with this requirement?. Anyone successfully connected a Wireless device to the hardwire home system?
 
I remember when this requirement first hit the codes there was some chatter among our local fire code folks who thought it was a "kart before the horse" kind of thing. This is outdated, and CA specific, but interesting:
 

Attachments

  • ib_ess_heat_detector_residential_code_final.pdf
    161 KB · Views: 5
... Here are my interrogantes: 1 Installing a Heat or Smoke detector inside a garage (at least with this really hot summer in las Vegas) is going to be annoying for the customer.

I don't see why. It's required to be a heat alarm, not a smoke alarm, so that it doesn't trip from dust and exhaust. If the garage is too hot for the heat alarm (typically 135F) then I think you have issues with garage ventilation, even in Vegas, and you probably shouldn't be installing batteries in there to begin with.

2 Any Idea how comply with this requirement?. Anyone successfully connected a Wireless device to the hardwire home system?

There are some wirelessly interconnected products available. We used one from X-Sense a couple times, but had to replace all the other alarms.

Also start telling all the GCs you know that new builds should include a heat alarm in the garage just in case.
 