The locks are for dorm rooms. They have a mechanical means of egress. The problem I see is if the batteries catch fire you will not be able to use the handle to get out. I would think this is a life safety issue being its the only exit in the room.
The mechanical means is to override the electrical means, and if power fails the door should unlock.
Is this latching system fire exit hardware? where designed to stay latched during a fire?
2009 IBC
1008.1.10 Panic and fire exit hardware.
Doors serving a Group H occupancy and doors serving rooms or spaces with an
occupant load of 50 or more in a Group A or E occupancy shall not be provided with a latch or lock unless it is
panic hardware or
fire exit hardware.
Exception: A main
exit of a Group A occupancy in compliance with Section 1008.1.9.3, Item 2.
Electrical rooms with equipment rated 1,200 amperes or more and over 6 feet (1829 mm) wide that contain overcurrent devices, switching devices or control devices with
exit or
exit access doors shall be equipped with
panic hardware or
fire exit hardware. The doors shall swing in the direction of egress travel.
1008.1.10.1 Installation.
Where
panic or
fire exit hardware is installed, it shall comply with the following: 1.
Panic hardware shall be
listed in accordance with UL 305; 2.
Fire exit hardware shall be
listed in accordance with UL 10C and UL 305; 3. The actuating portion of the releasing device shall extend at least one-half of the door leaf width; and 4. The maximum unlatching force shall not exceed 15 pounds (67 N).