Brian it could be a UPS, 192 just works out for 8 48-volt strings. Doesn't matter, either way. I have designed many UPS and DC plants, some AHJ require extra ventilation some do not. As long as there is ventilation, there is no real danger. The biggest issue I run accross is spill containment for flooded batteries.
As you say corrosion is not an issue. I do not use enclosed raceways for DC cable rather cable ladder. The only place corrosion is an issue is at the battery term plates, inter-cell connectors, and cables that connect to the term plates. I use lead coated compression connectors with no inspection holes and all cables and terminal connections treated with "NO-OX". Or in other words follow the manufactures direction to the letter, and use compression connectors with a crimping tool that uses either circumcial or hexagon compression dies, no "pinch compression. Burndy makes a full line of connectors and tools for DC power work.
Good Luck
Dereck