Battery to UPS DC cables

Status
Not open for further replies.

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
In NEC, what is max allowable distance between batteries and UPS which DC cables can run?
 
In NEC, what is max allowable distance between batteries and UPS which DC cables can run?

AFAIK there is no distance limit. But the system design should give you a maximum voltage drop over the battery circuit and you can use that to find the maximum distance for any selected wire size that meets or exceeds the ampacity requirements.
The conductors should also be protected by an overcurrent device of some sort, as close to the battery bank as possible.
 