240.24(B)(2) Branch-Circuit Overcurrent Devices. Where electric service
and electrical maintenance are provided by the building
management and where these are under continuous building
management supervision, the branch-circuit overcurrent devices
supplying any guest rooms or guest suites without permanent
provisions for cooking shall be permitted to be accessible
only to authorized management personnel.
(C) Not Exposed to Physical Damage. Overcurrent devices
shall be located where they will not be exposed to physical
damage.
Informational Note: See 110.11, Deteriorating Agents.
(D) Not in Vicinity of Easily Ignitible Material. Overcurrent
devices shall not be located in the vicinity of easily ignitible
material, such as in clothes closets.
(E) Not Located in Bathrooms. In dwelling units, dormitories,
and guest rooms or guest suites, overcurrent devices, other
than supplementary overcurrent protection, shall not be located
in bathrooms.
(F) Not Located over Steps. Overcurrent devices shall not be
located over steps of a stairway.