Ryan, 250.104(C) refers to structural steel that is not intentionally grounded and may become energized. What he is describing IMO is that the building steel has been intentionally bonded to a grid, making it part of the electrode system.Originally posted by ryan_618:
Good. I left my code book at work today, but I know that 250.50 applies, and I'm pretty sure there was a change in the 2002 to section 250.104 that addresses bonding around joints in structural steel.
You wouldn't use it as a grounding electrode conductor, but you would use it as a grounding electrode. You are required to do so if it is available and is effectivley grounded.Originally posted by vanwalker:
still learning?? why would you use building steel as a grounding electrode conductor(gec)THANKS GEO