Heres what I have.
Existing service is 100amp 120/208v 3 phase
Lighting 600sq ft @3 va per = 1800va
signage (doubt it will be lit)=1200va
5 separate circuits for hair dryers @ 1800va each=9000va
20 receptacles @ 180va each=3600va
2 seated hair dryers@1800va each=3600va
1 microwave@1500va
1 mini fridge@400va
heat=15.8kva (larger load than the a/c)
This totals 37000va
37000/360=102.78
If I upgrade to 125amp should I be safe.
Existing panel is 125a rated. I could re use it.
Or.... am I cutting it too close.
Am I missing anything obvious?
Thanks
Existing service is 100amp 120/208v 3 phase
Lighting 600sq ft @3 va per = 1800va
signage (doubt it will be lit)=1200va
5 separate circuits for hair dryers @ 1800va each=9000va
20 receptacles @ 180va each=3600va
2 seated hair dryers@1800va each=3600va
1 microwave@1500va
1 mini fridge@400va
heat=15.8kva (larger load than the a/c)
This totals 37000va
37000/360=102.78
If I upgrade to 125amp should I be safe.
Existing panel is 125a rated. I could re use it.
Or.... am I cutting it too close.
Am I missing anything obvious?
Thanks