I am looking at building a 600 amp service (re-doing a 600 amp delta service). The utility company wants to do away with the delta service that is existing.
The existing service (as I was told) runs from overhead to underground into the building in 6" PVC with aluminum conductors.
I am to install a disconnect on the utility new utility pole. The current service does not have the proper number of conductors in the existing conduit, therefore copper wire will be required.
The service has been there for quite some time [concerned about removing the existing wires from approximately 80 feet of underground PVC].
I am currently figuring on whether runs of 2,000 kcmil THWN copper or paralleling 400 THWN copper as per cost, handling the size of the wires, & what will fit in the conduit.
As per table 250.66, it appears that 3/0 copper grounding (ground to us old timers) conductor will be adequate in either case (since over 1100 kcmil copper will be used)? :? BUT then per table 250.122, it appears that #1 copper (since 600 amp disconnect) ? :?
And then Table 250.102(C)(1) Grounded conductor (neutral) 12 1/2% of the area of the largest ungrounded conductor. 12.5% x 2,000 kcmil = 250 copper ? :?
Thanks for you'll input.
The existing service (as I was told) runs from overhead to underground into the building in 6" PVC with aluminum conductors.
I am to install a disconnect on the utility new utility pole. The current service does not have the proper number of conductors in the existing conduit, therefore copper wire will be required.
The service has been there for quite some time [concerned about removing the existing wires from approximately 80 feet of underground PVC].
I am currently figuring on whether runs of 2,000 kcmil THWN copper or paralleling 400 THWN copper as per cost, handling the size of the wires, & what will fit in the conduit.
As per table 250.66, it appears that 3/0 copper grounding (ground to us old timers) conductor will be adequate in either case (since over 1100 kcmil copper will be used)? :? BUT then per table 250.122, it appears that #1 copper (since 600 amp disconnect) ? :?
And then Table 250.102(C)(1) Grounded conductor (neutral) 12 1/2% of the area of the largest ungrounded conductor. 12.5% x 2,000 kcmil = 250 copper ? :?
Thanks for you'll input.