Below normal voltage on each phase

Status
Not open for further replies.

oscaro5

Member
Location
California
Occupation
Electrician
Hi everyone. Just wondering if anyone could give me some insight on what’s possibly going on. I’m thinking this is just undersupplied voltage from the utility company?

So here’s the setup. Residential single phase 120/240 system. Meter main is surface mounted outside with a single 200a distribution breaker. Nothing in the meter main was touched other than to pull out the old wires and refeed in new. The old were too short to reach the lugs. Panel was fed with 3x 2/0 and a #4 ground.

The 200a fed an old meter main that had been converted to a sub panel. This old meter main got demo’d and a new 200a sub got installed in its place but semi flush into the garage. Exterior pipe work was adjusted a bit.

Unfortunately no one checked voltage before disconnecting the old feeders… but now we have between 103-109v A or B to neutral and ground, 205-220v phase to phase. Lighting is flickering or won’t turn on throughout the house.

I’ve never came across equally low voltage on each phase. Voltages have been checked in the new sub panel as well as the meter main and are the same in both locations. Is this just a situation of weird coincidence and the client has been supplied with low voltage for some time now or could there be an issue I’m missing.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would check the voltage at the meter with no load. If it's too low then that's an issue for the poco to solve.
 

oscaro5

Member
Location
California
Occupation
Electrician
I didn’t have time today but will swing by tomorrow to run some tests with all loads off. Say it isn’t a service provider issue. I’m having a hard time thinking of what it could be. A loose neutral would give me a higher and lower voltage phase not an equal voltage. At this point just brainstorming before running more tests
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I didn’t have time today but will swing by tomorrow to run some tests with all loads off. Say it isn’t a service provider issue. I’m having a hard time thinking of what it could be. A loose neutral would give me a higher and lower voltage phase not an equal voltage. At this point just brainstorming before running more tests
It sounds like a supply voltage issue. Before wasting any more time on it you'll need to determine if your voltages are good at the source which in this case is at the metering equipment. I agree with you if it isn't the supply finding the answer may be tricky.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
230519-0919 EDT

oscaro5:

You have received good comments.

I wii assume the first place you can make measurements is in your main panel. Turn off all breakers, and open any fuses in the main panel. This puts no current load on the source. Measure the voltage directly on the conductors into the main panel. This means each line to neutral, line to line, and neutral to earth. This provides you with the source voltage no load voltage at the earliest possible point.

Next measure one hot line input in the same way, and load that phase somewhere with a 1500 W 120 V space heater. In my home that reading will drop about 1 V. Then move the meter to the other phase, and again do the load test. This opposite phase should rise about 1/2 V in my case.

If these results for you are about the same, then it is likely a transformer tapping problem.

Much greater changes likely means wimpy supply wires or impedance in the supply to or thru the meter.

You can also do the same test on the other phase.

Depending on your results you determine whether or not to call the power company.

..
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
230519-1201 EDT

oscaro5:

An additional point.

If your voltage is jumping around from 103 to 109 V over a short time, and you have no load changes during this period, then I would be concerned with what might be the cause. Further, if this change is on the input wires to the main panel, then I would assume an external cause.

.

.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
If the main is plug on, could be a burnt buss, may have been aggravated by changing the load wire on the breaker. Easy test is FOP. (Fall of potential) with the loads on, measure voltage on each leg from line to load, you should get close to zero volts. If you get several volts, the connection is bad.
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
A handheld hairdryer with some good alligator clips makes a nice little portable load bank

Don't steal your wife's though, you'll never hear the end of it.
 
Last edited:

oscaro5

Member
Location
California
Occupation
Electrician
Thanks everyone for the suggestions. Was able to take measurements on line side of meter the following day, readings were consistent across meter and main disconnect. Called poco and was told ongoing work was being done in the area. Voltage issues resolved the following day.
 