Bend radius for Fiber cables ( 2 Fiber Multimode 62.5/125mm)

Status
Not open for further replies.

transman2

Senior Member
Location
Brooklet,Ga.
Is it legal to install 6 fiber cables ( 2 Fiber Multimode 62.5/125mm) in a 2" LB68 with a bending radius of 4.4 inches. Cable diameter is .3. So if I use a factor of 10 x .3 that should be a 3 inch bending radius however I have 6 cables so does that change the outcome.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
The NEC has nothing to say about it.

-Hal
Yes, the purpose of the NEC is protection against electric shock and fire. Having your fiber working is beyond its scope.
I have done a lot of fiber installations, I had a 3 ring binder with data sheets on cable, patch panels, connectors, for reference on cable bending. There is a type of newer fiber called bend tolerant, but I hadn’t used it.
on your application, if it’s a short run, and you have enough headroom, ie what is your loss budget, you may be ok.
Could you use a deep NEMA junction box Instead of the LB?
 