JimmyDeanxs
Member
- Location
- Midwest
- Occupation
- EE
Hello,
I have a weird question about cable bend radius of 25kV 3/C & 3G cable entering a substation ATC chamber. I have a manufacturer recommended minimum bend radius of 21", structural team has left me approximately 12" from the top of the cabinet cable entry point to the top of the cable tray rung running above it. Question is, can the cable bend radius be fulfilled while entering the enclosure? Or does it have to be fulfilled before entering the enclosure so the cable enters on straight or perpendicular to the enclosure?
Unfortunately, I don't have a lot of resources or experience with these types of installations and EOR gives copy paste, "follow NEC requirements for bend radius" statements.
Any ideas or guidance is much appreciated.
I have a weird question about cable bend radius of 25kV 3/C & 3G cable entering a substation ATC chamber. I have a manufacturer recommended minimum bend radius of 21", structural team has left me approximately 12" from the top of the cabinet cable entry point to the top of the cable tray rung running above it. Question is, can the cable bend radius be fulfilled while entering the enclosure? Or does it have to be fulfilled before entering the enclosure so the cable enters on straight or perpendicular to the enclosure?
Unfortunately, I don't have a lot of resources or experience with these types of installations and EOR gives copy paste, "follow NEC requirements for bend radius" statements.
Any ideas or guidance is much appreciated.